I’ve got my hands on some second-had Wiwynn SV328R servers that I’m trying to make operational. I’ve installed Ubuntu Server 22.04.3, but cannot seem to be able to get the fans to run at anything less that 100%. Any insights as to where I might find the IPMITool raw commands for this machine would be appreciated.
Update:I found some info in the Mt. Jade docs online indicating that the 2S1P (2 Socket/1 Processor) configuration will run the fans 100%. A solution might be to upgrade the firmware and see if I can add another processor to make it a 2S2P. Curious to see if this is possible or if Socket 1 is hardware disabled. Anyone know where I can get the latest AMI firmware?
For me, the issue was the use of a NVMe drive model that was not on the Hardware Compatibility List… If you are running NVMe drives, try pulling them and powering on - obviously the machine won’t boot, but the fans should not go into hovercraft mode.
I have run both 2S1P and 2S2P with auto fan control, don’t know where you saw that 2S1P will run at 100% fan speed.
For a temporary workaround (with some problems/risk), you can set the fan speeds manually, but then it is on you if the processors overheat due to high load.
PERFORM AT YOUR OWN RISK
To disable auto fan speed setting:
ipmitool -I lanplus -H <raw IP, eg 192.168.1.XXX> -U username -P password raw 0x3c 0x03 0x01
Note the username and password are for the BMC login.
Then for each fan:
ipmitool -I lanplus -H raw_IP -U username -P password raw 0x3c 0x04 <fan number, eg 0x01> <rpm percentage, eg 0x19 for 25% speed>
The number of chassis fans varies by model… mine had 8. I highly suggest that if it is in fact unsupported drives, you replace them and go back to auto fan control.
To go back to auto fan control:
ipmitool -I lanplus -H raw_ip -U username -P password raw 0x3c 0x03 0x00
The UEFI BIOS for 1P and 2P Jade is in the file titled: Ampere SRP 2.10d.20230530 AptioV Binary Package available on the Ampere Customer Connect portal. You’ll need to register and sign an NDA for access.
Thanks for the pointer to the Binary Package. I’m hoping upgrading the firmware will fix whatever is going on with detecting the 2nd processor - the current firmware is pretty old.
@vikingforties , @rory_be , pardon the delay in getting back to this. I did try flashing the firmware, but after doing so, the BMC would report a nonsensical version number, and I would not be able to move further (sorry about the lack of specifics, it’s been a while since I banged my head against this). I’m hoping to get back to those machines in a week or two, but if any of this rings a bell with anyone, please give me some hints.